Sep 27, 2013Explorer
Tradeoff Mena.
You are trading longevity and abusability for CCA
I'll say it again - If you have an inverter high loading issue, purchase (3) group 29-31 AGM batteries and connect them for charging purposes via a "smart" paralleling solenoid, and disconnect with topping or equalizing via a switch.
I can produce EIGHT KILOWATTS of power with 3 AGM group 31 batteries for around 15 minutes. A longer run time would be umm not intelligent with batteries. My 2-volt cells can do it but it takes an F-650 stake truck to haul them.
L-16 batteries are built for 20 hour discharge rates not 5 hour or 5 minute.
You are trading longevity and abusability for CCA
I'll say it again - If you have an inverter high loading issue, purchase (3) group 29-31 AGM batteries and connect them for charging purposes via a "smart" paralleling solenoid, and disconnect with topping or equalizing via a switch.
I can produce EIGHT KILOWATTS of power with 3 AGM group 31 batteries for around 15 minutes. A longer run time would be umm not intelligent with batteries. My 2-volt cells can do it but it takes an F-650 stake truck to haul them.
L-16 batteries are built for 20 hour discharge rates not 5 hour or 5 minute.