Forum Discussion
pianotuna
Mar 07, 2016Nomad III
My catastrophic failure fuses are 350 amps each. My wire from the battery buss to the controller is not capable of sustaining 350 amps, so I would fuse to the wire size between the controller and the battery bank. The rule is "always fuse to the wire size".
In addition, since I have twin battery banks and switches to select where the solar harvest is sent, I have fused to protect the lovely switches that have led's in the stem. This approach worked to my favor when a technician managed to wire my system for 24 volts. I lost one Castrophic failure fuse, the reverse polarity fuses in the converter, and one of the fuses protecting the switch on that "leg".
Perhaps some one might consider this a belt and suspenders approach, but it paid off *big time* for me.
In addition, since I have twin battery banks and switches to select where the solar harvest is sent, I have fused to protect the lovely switches that have led's in the stem. This approach worked to my favor when a technician managed to wire my system for 24 volts. I lost one Castrophic failure fuse, the reverse polarity fuses in the converter, and one of the fuses protecting the switch on that "leg".
Perhaps some one might consider this a belt and suspenders approach, but it paid off *big time* for me.
2oldman wrote:
If I have a catastrophe fuse on the battery +, why do I need one on the controller wire to the buss/battery?