Hi,
Allowing for inverter losses it may draw 135 amps from the battery bank. The Peukert corrected amps are about 247 amps given a 360 amp-hour battery bank.
The question is how long can the inverter sustain the surge? If it is 1/10 of a second that's pretty much useless. If it is ten minutes--that's a quite respectable amount of time.
Allowing for inverter losses it may draw 135 amps from the battery bank. The Peukert corrected amps are about 247 amps given a 360 amp-hour battery bank.
The question is how long can the inverter sustain the surge? If it is 1/10 of a second that's pretty much useless. If it is ten minutes--that's a quite respectable amount of time.
JRRNeiklot wrote:
You're right, input power is 1350.
The inverter is actually 2,000 watts/4000 peak.