With my Magnum 3000 inverter, to aces the load share do one have both the charging and the inverting on at the same time? I want to be able to run my air conditioner of my Honda 2.2 companion, which i...
Slownsy wrote:You should be running the A/C and charging the batteries through the magnum. The Magnum has load sharing to supplement power from the battery to start the A/C. Once running all excess power will be used to charge the battery.
The Honda will run the air conditioner ok, if batteries not down. I am probably mixing to issues together. I run the generator to charge batteries with the charger inbuilt in inverter, charges at about 100A. I also run generator to run air conditioner, but if batteries are down the load is to high for it. My setup is unique in as much as being in Australia we have 240V, so has a manual double trow treway switch, op 110V or generator, central of and down 240V true a step down transformer.
My question is the inverter has load sharing as if inverter can’t support the load it will take some power from batteries, how do this work, is it automatically done .