road-runner wrote:
From the picture it sure looks like it was already bonded at the factory.
120VAC Neutral is not bonded to the 120VAC socket's Ground screw, but to what look's like the case ground.
EDIT: That's definitely the case ground.
And the case ground is wired to the frame/chassis ground, which is wired to the 120VAC Ground back at the 120VAC distribution centre, which ends up back at the inverter.
So yes, ultimately, when running the inverter, it looks like 120VAC neutral and ground are bonded.