Forum Discussion
brulaz
May 05, 2017Explorer
Tried the Kisae by plugging in the trailer's 120VAC input cord.
This would create a neutral to ground bond via the Kisae's neutral-to-case, case-to-chassis and then the trailer's chassis-to-120VAC_Grd connections.
And sure enough, my Prog. Dyn. EMS accepted it. This EMS requires a bonded input.
On the other hand, if I don't use the trailer's 120VAC system with it's ground-to-chassis, and plug some appliance directly into the Kisae. It will NOT be bonded. :R
This would create a neutral to ground bond via the Kisae's neutral-to-case, case-to-chassis and then the trailer's chassis-to-120VAC_Grd connections.
And sure enough, my Prog. Dyn. EMS accepted it. This EMS requires a bonded input.
On the other hand, if I don't use the trailer's 120VAC system with it's ground-to-chassis, and plug some appliance directly into the Kisae. It will NOT be bonded. :R