This is what i was thinking Is 300amp breaker the right size?
What size wire will you be using? That's the main purpose of the fuse--to prevent a fire from the wire overheating in the event of a short circuit.
300A is a reasonable ballpark value, though larger might be better as most inverters have a surge capability somewhat beyond their nominal rated capacity. (Well, decent inverters do; all bets are off for questionable unknown brand inverters from overseas.)
Edit: The inverter instructions may have some recommendations on power lead wire size and fusing.
I am planning on using 1/0 wire