- eendExplorerI installed a 1000 watt inverter, I wanted to use 8 gauge wire, but that is hard to find and expensive.
But I bought a cheap set of 12’ 8 gauge booster cables for $13.00 at our local Canadian tire store,
Cut the clamps off, and soldered new round connectors on , and works perfectly. - wa8yxmExplorer III
larry cad wrote:
I=P/V
I=AMPS
p=POWER (OR WATTS)
V=VOLTS
I=425/12=35.4 AMPS
10G wire is rated 30amps.
I would go with #8
Add 10 percent for converter loss and overhead So the "rule of thumb" i use is figure AC watts / 10 volts
For that inverter I'd use standard automotive battery cables (4GA) for runs up to around 5-8 feet.. Longer runs bigger wire.. I'd not go shorter.
One Edit.. I said I would.. I also DID. When I had an inverter in that size class. - afidelExplorer IIPersonally I'd use an automotive auto-resetting breaker over a fuse. They are much more waterproof, less of a chance that they'll ruin your outing by nuisance trips, and are just much less of a hassle. At small scales the cost difference is immaterial, for $9 you get 4 fuse holders or 2 breakers, compared to all the other costs in the project it's noise.
- MrWizardModerator8ga minimum 6ga would be better, 40a*12v= 480w ,
If the only thing being powered is the TV and cellphone chargers you can use 10ga, but i prefer going larger as you might someday want full max use from it - Microlite_MikeExplorer III find charts for wire size to often be confusing and too broad in their recommendations.
For 12 volt circuits (automotive/RV) I prefer this online calculator.
https://www.wirebarn.com/Wire-Calculator-_ep_41.html
Parameters needed for calculations are the maximum amperage of the device you're going to power (which for Inverters needs to take into consideration surge capacitiy),and the length of the wire in BOTH directions as it's a DC Circuit. If using a chassis/frame ground at each end then just use the total length of the wire between battery and device PLUS the wire from battery to frame and device to frame.
This calculator also shows voltage drop for each wire size and the max length at stated amperage to achieve the desired max percentage voltage drop. - theoldwizard1Explorer II
time2roll wrote:
With 105C insulation of marine grade wire the #8 is good for 80 amps if not in a bundle.
#10 is adequate if the distance is on!y a few feet. 40A fuse, as close as possible, to the battery.
Marine grade wire is pre-tinned and should never corrode. It is worth the extra cost. Gdetrailer wrote:
NEC allows #8 wire on a 50 amp breaker if the distance is short.
50A fuse would be for 6Ga wire, not for 8ga-26ga wire.
With 105C insulation of marine grade wire the #8 is good for 80 amps if not in a bundle.- pianotunaNomad III
freewayrandy wrote:
Thanks for all the info. Pretty lame on electrical here. Inverter primarily for TV. What would be recommended fuse size?
#8 wire with 40 amp fuse (slow blow optional), or a 40 amp breaker. Place the fuse/breaker as close to the battery bank as possible on the positive lead.
We always fuse to the wire size. - GdetrailerExplorer III
time2roll wrote:
50 amp fuse close to the battery or power source. I agree with #8 unless the distance is long go #6 wire.
Fuse to the wire size, the idea is to protect the wire not the device hung on the wire.
SEE HERE
"Why use a fuse?
A fuse provides a safe and cost effective way to protect an electrical device or installation from electrical overloads which could damage components or wiring and potentially cause a fire."
Basically you want the fuse to blow out in a controlled manor well before the entire wire becomes a fuse.
Per HERE
"Fuses normally protect wires from burning and setting fire to things"
Per HERE
"When specifying a fuse for an after-market application, the key consideration is that the fuse should be the weakest point (i.e. lowest rated component) so that it always blows before any damage occurs to other parts of the electrical circuit. However, you also do not want the fuse to keep blowing under normal operation (known as a nuisance blow), so the two elements to consider are:
The current rating of the smallest cable in the circuit
The current draw on the circuit under normal expected operating conditions
The fuse rating should lie somewhere between these two values to allow normal operation but blow on overload. For example, if the normal expected current draw is 10A and the cable size is 25A, then a fuse rated at 15A would be appropriate."
50A fuse would be for 6Ga wire, not for 8ga-26ga wire.
Granted, bare UNinsulated wire can sustain higher current than insulated wire, but, it isn't like one is going to install and use UNinsulated wire for this use.
Where to place the fuse?
Generally, as close to the power source (IE 12V battery in the case of the OPs situation) as possible, I have often seen references of 18" or closer to the battery..
On edit..
I will also add that if you have wire which has more capacity than the expected load, you can use a lower amperage fuse.
In other words, if you had 8 ga wire which would typically be fused at 40A but your device (like a 400W inverter) draws 35A at max full load you could fuse to the max load of the inverter which would be 35A.. But cut that too close and you may get nuisance blown fuses..
The idea of using larger wire sizes than needed is not to handle more current, but to lower the voltage drop seen by the inverter.. Just .1V extra drop in the wire can make the difference between the inverter working or shutting down in 12V systems. - GdetrailerExplorer III
freewayrandy wrote:
A friend gave me the inverter and didn't have the manual but your info helps. Thanks.
Google search the make and model of your inverter and add manual to the end of the search string and by the magic of the wobbly web you most likely will find a online PDF of your inverter manual. You can download the PDF and open it with Adobe reader (free), Open Office (free), Libra Office (free) and even newer versions of MS Office (not free) are able to open PDFs directly..
HERE is a search I did for Cobra 400W manual (you didn't give name and model so I randomly selected a brand and model)..
HERE is the first result of that search which brought up "manualslib.com" which is a huge online library of manuals..
For fuse sizing, you can follow NEC wiring conventions.
10 ga wire = 30A fuse or breaker
8 ga wire = 40A fuse or breaker
6 ga wire = 50A fuse or breaker