dougrainer wrote:
I asked about 50 or 30 amp service because you CANNOT add excess amp draw to a 30 amp box. 30 amp RV boxes are designed for the 30 amp load in the RV and are designed to split the loads to total 30 amp. If you are trying to run an extra 20 amp circuit and appliance you will overload and trip the Main 30 amp breaker in the Breaker box or the CG pedestal pole breaker. Not really dangerous as the breakers will do their job but just an annoyance. Doug
I believe NEC allows max 5 branch circuits with a 30 amp main. The breaker ratings and appliances in a 30 amp RV very typically can exceed 30 amp draw. Manual power management is needed or the lights go out.
Regardless of NEC I added 2 more breakers but they are for items very rarely used. Never an issue.