Depends! :)
Relion says:
"More Usable Capacity 25-50% more capacity than lead-acid equivalent."
Many say 100% is usable with LFP, but many users here like doing 20-90s for 70% range in real life, so that compares with 50-90s using 6s at 40% range. You could do 40-90s at 50% range with your 6s too.
70 is 30 more than 40 and 30 is 75% of 40.
70 is 20 more than 50 and 20 is 40% of 50.
You also have "inverter usable" vs "furnace usable". The LFP stays above inverter alarm 11v to a lower SOC than 6s do. But you can go lower with the 6s and still run the furnace even though you can't do inverter anymore at that lower SOC.