I would suggest replacing the feed to the garage and then installing the RV receptacle off that.
You could use RHH/RHW/USE wire which is rated for direct burial. I would use #6. Yes, slightly overkill(50 amp). yes, #8 would work(40 amp).
The ground wire can be smaller. It would be calculated on the amperage of the circuit breaker in the source panel. A #10 ground wire would be sufficient for up to 60 amp circuit breaker.
I would install and additional ground rod at the detached garage for a little extra protection.