You probably ought to bond the inverter case directly to the chassis ground; I suspect that's required by the NEC. I believe it is for converters, at least, and the charger part of the inverter is essentially the same thing. I doubt very much this will prevent the GFI from tripping.
It sounds like the inverter is either causing a leak to ground or bonding neutral and ground somehow. If the charger output isn't isolated from the input power properly, I could imagine it might be a sort of ground fault. Likewise, if the inverter part is bridging neutral and ground, that could very well be an actual ground fault.
(All of that is not terribly helpful, I realize; it's pretty much just reiterating your initial statement that the inverter seems to cause a ground fault.)
Do you get the trip if the output of the inverter is left disconnected—i.e. if you don't plug the shore power cord into it?
It sounds like the inverter is either causing a leak to ground or bonding neutral and ground somehow. If the charger output isn't isolated from the input power properly, I could imagine it might be a sort of ground fault. Likewise, if the inverter part is bridging neutral and ground, that could very well be an actual ground fault.
(All of that is not terribly helpful, I realize; it's pretty much just reiterating your initial statement that the inverter seems to cause a ground fault.)
Do you get the trip if the output of the inverter is left disconnected—i.e. if you don't plug the shore power cord into it?