valhalla360
Aug 18, 2020Navigator
3 tons wrote:valhalla360 wrote:
So what is the goal of setting up a 24v system...if you aren't using 24v for all the DC loads?
24v systems are becoming more common on large yachts but that is because they have high wattage devices that are a long way from the battery bank and the voltage drop due to high amperage becomes a problem (Ex: Anchor winch might be 40-50ft of cable from battery to winch and a small winch might draw 250amp. By increasing the voltage to 24v, that drops to 125amp. They also may have electric sail winches, bow thrusters and other high wattage devices drawing hundreds of amps at 12v
By comparison, a slide out motor might draw 30amps and that's one of the bigger DC loads on an RV.
You’ve raised an interesting point here, one that I’ve often wondered myself?
Though I do not have long wire runs in my truck camper...I do occasionally run my 11kbtu air cond from the battery, but the biggest concern here is harmful LRA momentary voltage sag which can be reasonably addressed with a soft-start and with the rather stable voltage profile of LiFePo4...
FWIW, Victron BMV measured (at 12v) a LRA instantaneous pulse of 96a and steady running amps (after 12 min) of 88a...Using 0004, 6’ round trip cabling...
3 tons
If the goal is to run a 120v AC device off inverter, the amperage is usually addressed by placing the inverter close to the battery bank and feeding from battery to inverter with large cables...since it's only a few feet, voltage drop is usually not a big deal.
By contrast on a large cruising boat, the battery bank is typically near the stern and bow thrusters and anchor winches are at the opposite end of the boat necessitating long DC cabling runs which causes voltage drop issues.
Having RV issues? Connect with others who have been in your shoes.24,397 PostsLatest Activity: Jan 16, 2025