My generac diesel generator only runs with prime button

Diesel generator only runs with prime button held down model 004270-3.
Oil level and coolant are fine as the breaker and 14 amp fuse. The thing that perplexed me is why it runs about 30 second after running after priming, it will run if holding down the start button.
  • Matt_Colie wrote:
    In general terms, that prime button by-passes some safeties. There is probably something like a low oil pressure switch that wants some attention. OR, you could jumper in the prime circuit and see what breaks first.

    Matt

    At work we used to say the worse the problem gets the easier it is to find.