Quote from your info L1 and L2 are rated for 35 amps each
I don't care what the seller , Mfg, or distribute says
But 35 amp contacts will not carry 50 amps
So that is not a 50 amp switch
But yes you should be able to wire that to the Onan genset
But if you ever plug into 50 amp shore power which is connected to a double pole 50 amp circuit breaker, be careful to keep you loads down to 30 amps per leg
I don't care what the seller , Mfg, or distribute says
But 35 amp contacts will not carry 50 amps
So that is not a 50 amp switch
But yes you should be able to wire that to the Onan genset
But if you ever plug into 50 amp shore power which is connected to a double pole 50 amp circuit breaker, be careful to keep you loads down to 30 amps per leg