It is normal for the converter to do a few more amps than rating when the converter is close to the batteries on fat wire. My old Paramode (RIP) did 62 and my PowerMax 100 does 104. Even my Parallax 7355 does 56 for running a load (not when charging a battery though, which limits the output to the 40s on its longer wiring)
For fast charging the T-105s, IMO use the Trojan spec of 14.8v for Vabs and leave it there till amps taper right down, then drop the voltage to your Float spec voltage as adjusted for temperature. IAW do not do the absorption stage at 13.6, do it at 14.8
Absorption Stage (when amps start to taper once battery reaches close to 14.8v) should start at about 70% SOC with 64/225 = 28% charging rate so a good portion of the recharge from 70 to 100 will take place with the amps tapering at constant 14.8 volts.
On the unit itself no load bench, put the voltmeter in the output terminals and twiddle the knob, using a marker pen to mark around the knob some voltages like 13.6, 14.8.
When you are connected to the battery, the unit's meter will show a variation of the "converter voltage" so when you want to set the "real converter voltage " with the knob you can use your marks around the knob.