shane102's avatar
shane102
new power max converter, problems
Replaced wfco 8955 converter with power max pm4b-55-mba converter. I put the new PM in today and followed the testing directions.
Step 1. With only shore power hooked up and all DC fuses pulled and battery disconnected (No load): voltage reads 14.74 on output side and no noise from converter. Directions say it should read 13.6 +/- .2
Step 2. with fuses in and battery hooked up and shore power on: voltage reads 12.54 on output side and the converter starts humming. Nothing in rv is turned on. Voltage at batteries read 12.54. Directions say voltage should be the same or close.
shut down all power at this time.
Voltage at disconnected batteries read 12.48.
first question is: the PM converter wires that hook to output side of fuse panel (DC side) are white and blue and both are 10 awg. I hooked blue wire to positive connector and white to negative. Is that correct?
Not sure why at step 1 the voltage is reading 14.74 with zero load? And not sure why at step 2 the converter is humming with nothing on?
I will be calling best converters in mourning. Any help, please.
  • shane102, the unloaded circuit voltage is going to be higher than the loaded circuit voltage. Sounds normal to me.
  • BFL13, why would it read 14.6ish when first turned on if the batteries are disconnected and no load of any kind.
  • Yes, at the batteries verify that the positive from the converter is going to the positive on the battery.
  • Humming noise is not the fan. I can see the fan and it does not move. Humming sound is something else. Fan is free when I turn it by hand. The only difference in the lower portion of new and old is old has one red and one white wire for + and - to connect to output side, the new PM has one blue and one white wire.
    for checking polarity at batteries, are you talking about the converter supplying voltage/current to batteries to charge them. If so then no I have not.
  • Since there is no color schedule of wires included with the installation instructions or the unit, we can't say if blue, white, green or pink are to be connected to which phase of the RV's distribution panel or battery.
    If you cant remember which wire is to be connected to which phase, testing for continuity to ground with those two wires would tell you the difference. One will have continuity, one will not.
  • AFAIK it should read 14.6ish when first turned on, then after 15 minutes it should drop to 13.6 unless the batteries need charging.
    If you have battery voltage at the converter "output" then the converter is not on at all (still getting the 120v input?) or there is an "open" in the path. Perhaps the new "lower portion" is not connected quite right the same way the old one was?
    The "noise" should be its fan, which is temperature triggered. It will come on more often when it is doing the 14.x voltage.
  • Have you verified polarity to the battery?
    Open lead voltage sounds high, but that could be your meter. Do you have access to another meter to check?
  • Sounds normal to me. Although your battery does not seem to be getting any power. Did you check fuses?
Having RV issues? Connect with others who have been in your shoes.24,288 PostsLatest Activity: Jan 09, 2022
