Chris Bryant wrote:
According to the ***Link Removed***, the HJGAB-904 is 120 volt only.
Any way you can separate the other loads while on generator?
All loads are fed by the battery bank/inverter. 75% of the time, the solar panels/batteries/inverter supply is sufficient to meet the load demands. Only over a period of heavy overcast days and/or when utilizing higher demand equipment does the generator get started. So separating out loads would be onerous and entail running much more cabling not to mention having to start the generator for some loads but not others. I guess my last question is: is there any way to take advantage of the 2 - 30amp breakers or are the two legs never to meet?
Thanks for you input.