MrWizard wrote:
sure wish i could get a look at the wiring diagram
IF that is the one i am thinking of you will read ZERO or near ZERO across hot lead leads 1 & 2 going to the (2) breakers
the generator is capable of 120v 54 amps, but you are trying to pull to much from one 30a breaker
IF it measures zero across the hot leads and 120v from each hot to neutral
you should be able to connect the hots to together with (1) 50amp breaker
the problem is me doing something i know how to test for and do correctly
and telling somebody else its OK ?
the hgjab-904 is an emerald microlite belt drive, not the model i'm thinking about
still if its zero volts across the (2) breakers
you should be able to replace with a single 50 and connect them together
as the are already connected internally
and that is key to the whole thing
AH! Ok, now you're talking the language of my good friend. I'll pass your post along to him and get him to do the analytics next time he comes in to do some fishing.
Thank you very much.