wnjj wrote:
Chris Bryant wrote:
I thought of one other scenario that could explain that behavior other than bad adapter, but I really doubt it's the case- that would be a bad neutral in the rig- full 50 amp/240 vac service would give a virtual neutral, but the loads would have to be well balanced or the voltages would be all over the place.
Possibly...but I would think there would be nothing working while on the 30A service. Both hots of the 50A plug would be in phase with an adapter that supplies both from the 30A.
The only explanation that seems to make sense is an adapter that doesn't feed both hots.
Yeah- you are correct. I forgot that one leg does work...
It must be the adapter/cord interface.