ryankenn wrote:
The only issue with controllers like this is the charge circuit is too robust. This unit, even the smallest can draw 60A AC maximum. Being on a 20A circuit I need to limit how much it draws when charging. Since it can run from a generator of questionable voltage I am going to send them a message to see if that input would be more suitable.
The input draw is adjustable, you can set two different input draws one for utility and one for generator depending on their capacity.
AC Current Settings
The AC current settings, Grid Input AC Limit and Gen Input AC Limit, control the amount of current that the inverter draws from the source. Adjust these settings to match the input circuit breakers.
? The adjustment is meant to protect a generator or source that cannot supply enough current for both charging and loads. If the combined charging and loads exceed the setting, the inverter will reduce its charge rate and give priority to the loads. If the loads exceed this number on their own, the charge rate will be reduced to zero.