time2roll wrote:
otrfun wrote:
If it is 0 percent, is it generally correct to assume that 70 minutes at 25 amps would discharge the battery to roughly 50 percent?
battery will be a little less than 50%. It is constant amps not constant power. Actual power extracted diminishes as voltage tapers off. More power is extracted during the first 70 minutes vs the second 70 minutes.
They are not the same measurement, but when you do a draw -down at the "20 hr rate" based on the rated AH, you have the same question.
" Is it at 50% capacity when you run the 20 hr rate for 10 hours?"
I have done this often to test my batteries as they age to see how much capacity they really have by now. I run them down at their 20 hr rate (eg 5 amps for a 100AH battery) and see if it takes 10 hrs to get to 50% (as measured by hydrometer SG, AND confirmed by resting voltage per battery specification.) If it only takes 9 hours to get to 50% then they are 90% as good as new.
The usual blurbs on batteries show that it is supposed to be linear for discharging, but it is not linear for charging back up. So linear discharge should mean you are half -way down at the 10 hr mark out of 20 hours.
Same would be true using RC if you draw down at that RC constant rate.
However, in real life it seems to be a bit more complicated, where they seem to run down a little faster after the first 10 hours (if you over-shoot) which suggests it is not so linear.
Therefore it could be that 10 hours is more than half way out of 20, which seems silly, but we are talking batteries here! :)
Somebody who has more experience going below 50% might be able to confirm or deny that, but that is what I have (maybe) noticed--and I do pay attention while I am doing the tests.