Good morning from a snowy North Carolina. I have a 2006 American Tradition 40Z.I have a problem with my Magnum energy system it is showing a backfeed fault on the remote and the generator will run but no power to anything. Has any one else had this problem any help would be appreciated.Thanks Ron
Ron,
I'll give it a shot....not knowing how your system is wired. The 'backfeed' fault says that the inverter output has sensed an AC voltage on it's AC output. The inverter has shutdown due to the fault and you will need to perform a 'manual reset' to the inverter.
To do a manual reset:
Hold the 'power on' button down for 15 seconds until the inverter status led begins to flash, then release the 'power on' button and the led should stop flashing.
Hopefully everything will work forever after....If not you will need to check for any sub-panel that the inverter's AC output is attached to, any circuit breakers shorted, wiring shorted, etc.
Happy Travels,
Lew