DieselBurps wrote:If the Yamaha 2000's operate like the Honda EU2000's, there's only a minimal increase in inrush current when the units are paralleled. Yes, the continuous current output is doubled when the Hondas are paralleled; unfortunately, the inrush current only increases 10 percent, if that.
Curious if this is possible or anyone has done this. Currently I can run my Coleman mach air conditioning unit in my truck camper off just one yamaha 2000 watt generator but it's not happy about it and from the sound I can tell it's maxed out. I am wondering if I were to run two 2000 watt generators in parallel could I do it with the eco throttle on? It seems like this would be possible since both generators are putting out 26 amps and given the fact I am able to start it and run the ac with just one.
Why? I couldn't tell you. Bottom line, a paralleled pair of Honda EU2000i's may still need to be run with the Eco mode off to start some 13.5k - 15k RV a/c units with higher LRA's (typically those with LRA's of ~60a and higher).