rjsurfer wrote:
Is there an advantage to using the 50 amp power pole receptacle?
Yes. If you have an RV with 30 amp service, it is usually preferable to plug into a 50 amp pedestal if available, using a 50/30 amp dogbone adapter. Reason is, the 30 amp receptacles are often well used and abuse in comparison and can be a poor connection, resulting in heat. Always use dogbone type adapters and not the "puck" style.
As above, if you have a 50 amp RV, do NOT use an adapter at the power inlet and run a 30 amp cord to a pedestal and then use an adapter to get back from 30 amps to 50 amps. That would be allowing up to 100 amps on a 30 amp rated cord. End result = heat, smoke & possibly flames... :E
If permanently converting to 30 amps, you *could* modify the 50 amp panel and install a 30 amp power inlet or a hardwired cord (through a mousehole). Or use a 50/30 amp dogbone adapter at the power inlet and then run a 30 amp cord out to a pedestal. This does introduce an additional connection in the power circuit which could potentially eventually lead to an overheated connection. Periodically check for heat.
Other than the weight & bulk, I would keep the 50 amp cord as an extension cord or spare along with the appropriate adapters.
I would also add that finding 50 amp pedestals in CGs can be very hard (unless you go to high-end ones, casinos, some gov't CGs, etc.). Up until 2005, the NEC only required 5% of RV Parks (CGs) to have 50 amp pedestals and then it was changed to 20%. Since the majority of CGs are 2005 & older, it's a good idea to be able to run on 30 amps. And if you have only one AC unit, there's little advantage to 50.