3_tons
Jul 22, 2018Explorer III
SoundGuy wrote:3 tons wrote:
When generator is running, theres 125v, but only up to the inverter - the inverter for some reason does not ‘recognize’ the gennys output, so will not pass it thru to the campers circuits... Sounds like maybe a bad ATS inside the inverter...
More likely the ATS and / or inverter isn't happy with your EU2000i's floating neutral output. Have you tried bonding the genset's output?
Thx, So if I have you right you are referring to the fact that gennys (passive) floating neutral may not be bonding when not on shore power, correct??...if so, I’m not quite sure of a way around this...
Upon edit (thinking through this a bit more....), it would seem that the genny’s floating neutral would passively ‘un-bond’ whenever it sensed Shore Power, and would again re-bond’ otherwise. Inverter also has a floating neutral, but I fairly sure that it has been disabled (utilizing its disable option) at time of install...