Pianotuna writes
“Hi Gde,
Do the ones you listed handle 30 amps and/or 50 amps?”
“Technically” in a “round about way” YES.
But not the way you would think of..
You are thinking of an external mystery box that you plug your RV into via the shore cord..
The devices I listed are power/surge strips in which you typically plug individual items into.. But the “protection” they offer actually EXTENDS to EVERYTHING on that power circuit provided the power strip is plugged into an outlet AND turned on AND the protection devices are functioning..
The devices which Mex mentioned are placed in PARALLEL to the “circuit” or power lines if you like.. They are not “In series” and therefore ALL the protection is available BEFORE AND AFTER where the protection devices are inserted into the circuit.
They work by SHUNTING voltages that exceed their breakdown voltage threshold TO GROUND, is also known as “clamping”.
To be very clear, NO “surge protection devices” can or will protect against a DIRECT LIGHTNING STRIKE even several miles down the power line!!! They only protect from lightning INDUCED surges (indirect lightning strikes)..
I am not aware of any device that would be reasonably priced that would handle a direct lightning strike, therefore the “best practice” of preventing damage during a strong thunderstorm is to physically disconnect your electronic devices from the power company (IE unplug shore power or TVs/entertainment items)..
A good explanation of MOVs can be found
HEREFrom the website above..
“The Metal Oxide Varistor or MOV is a voltage dependent, nonlinear device that provides excellent transient voltage suppression. The Metal Oxide Varistor is designed to protect various types of electronic devices and semiconductor elements from switching and induced lightning surges.
When exposed to high transient voltage, the MOV clamps voltage to a safe level. A metal oxide varistor absorbs potentially destructive energy and dissipates it as heat, thus protecting vulnerable circuit components and preventing system damage. Varistors can absorb part of a surge.
About the MOV – Metal Oxide Varistors
A MOV contains a ceramic mass of zinc oxide grains, in a matrix of other metal oxides (such as small amounts of bismuth, cobalt, manganese) sandwiched between two metal plates (the electrodes).
They can be connected in parallel for increased energy-handling capabilities.
MOVs can also be connected in series to provide higher voltage ratings or to provide voltage rating between the standard increments.
A Metal Oxide Varistor remains non-conductive as a shunt mode device during normal operation when voltage remains well below its “clamping voltage”. If a transient pulse (often measured in joules) is too high, the device may melt, burn, vaporize, or otherwise be damaged or destroyed.”Typical simple in circuit usage (symbol with SIOV)..

Picture of MOV

Transit voltage bidirectional diodes and gas discharge tubes are also placed in parallel just the same as MOVs, they work similar to MOVs but with different speeds.
Cheap surge protection power strips ($8.99) typically only have MOVs and the more expensive versions ($30 and up) will have MOVs, Bidirectional diodes and gas discharge tubes.
When dealing with a 50A RV shore cord you simply need two surge strips and make sure that one of each is connected to L1 and L2..
One of the reasons as to why those external 30A and 50A “surge protectors” cost so much is the fact they ARE designed for the RV “industry” and they often offer other “protection” like OVER and UNDER voltage disconnect and or AVR (Automatic Voltage Regulation)..
To be clear Mexs idea does not address OVER/UNDER voltage nor does it address AVR..
If you dig around, you can find plug in surge/power strips which do have over/under voltage disconnect protection and if you want AVR many good UPS units actually provide surge AND AVR functions.. Just beware with these you must plug in items to be protected downstream to get the “protection”..
An additional way to add “surge protection” is to install a “whole house” surge protector in your RV breaker panel..
You can get a Leviton 51110-SRG Residential Surge protection Panel for as little as $43 from
HERELooks like

Typical home installation requires the use of two 120V single pole breakers that go to the device.. In a RV you would need only one single pole 20A breaker for a 30A shore power connection and only need to wire L1 or L2 of the protector.. Or if no extra breaker spaces available you could simply wire to any of the breaker protected branch circuits in a pinch.
You can view the installation manual for the Leviton protector
HERE