Using Atwood 1H2C Thermostat with Dometic A/C ??

I am attempting to replace a Duo-Therm Thermostat Model# 3107612.008 with an Atwood Model# 1H2C. Neither the furnace, A/C compressor, or A/C fan will operate with the Atwood. All functions are good with the Duo-Therm.

The Atwood documentation claims that it "has been designed to operate standard air conditioning units in conjunction with an RV furnace".

Furnace: Atwood Model# 8535IVDCLP
A/C: Dometic Model# 620426.331

Duo-Therm Thermostat connections:
Terminal Wire
-------- ----
+7.5 Red
Cool Yel
Fur Wht
Fan Hi Blu
Fan Tan
Gnd Grn

Atwood Thermostat connections:
Terminal Wire
-------- ----
1) Gnd Grn
2) n/c
3) +12VDC Org (voltage verified)
4) +7.5VDC Red (voltage verified)
5) Compressor Yel
6) Fan Hi Blu
7) Fan Lo Tan
8) Furnace Wht

1) The Orange wire in the thermostat cable was not used for the Duo-Therm thermostat installation, and was not connected at either end of the thermostat cable run. The Atwood thermostat requires a source of +12VDC. The Orange thermostat wire is now connected to a wire labeled "+12VDC" in the A/C wiring compartment. This "+12VDC" wire appears in a cable from the coach wiring, supplying the A/C unit. Have verified that the Orange thermostat wire is at +13.5VDC with respect to the Green ground wire. The Atwood thermostat display "powers up" upon connection of the Green and Orange wires. The Orange thermostat wire IS NOT connected to "CON 1" of the A/C controller, which apparently would be the case for a Heat-Pump / Heat-Strip application, which I do not have.

2) I note that all of the thermostat connections (with the exception of the added Orange +12VDC wire) connect directly to the A/C controller. The A/C controller provides a pair of terminals which connect to the furnace's thermostat circuit. The furnace does not connect directly to the thermostat.

3) Have experimented with the "heat" function with no thermostat connected to any wiring. The furnace goes "on" when the furnace "White" wire is connected to the ground "Green" wire.

4) Have experimented connecting to the Atwood t-stat all wires except the furnace "White" wire. The A/C compressor and A/C fan do not operate.

5) On the Atwood thermostat, there is an undocumented "dot" in the lower left corner of the display which appears to be a "Call" indicator. This appears to be functional, is "on" in "heat" mode with setpoint above room temperature, is "on" in "cool" mode with setpoint below room temperature, otherwise "off".

Does anyone have any ideas why the Atwood won't work?

40 Replies

  • Atwood says I need to run another 12v lead to the thermostat, will see if that works.
  • Bill Martin, did chris' suggestion work for you? I have the same thermostat and want to try installing it. Do you have the 2 speed fan for the AC?
  • Atwood provided faulty instructions- the so called 7.5 volt is not used- terminal 4 on the thermostat needs to be hooked to ground. If Atwood had just used standard terminology it would be easier- they show terminal 4 as relay common- a.k.a. rc and rw combined. Because DuoTherm switches the ground side of the relays, you need to provide a ground to rc and rw.
    Given that they made that error, I'm not sure if the high fan will work correctly, because DuoTherm uses a relay for fan, then a relay to toggle between high and low. RVP uses a high relay and a low relay- IOW, both fan relays need to be energized for high fan for DuoTherm, single relays need to be energized for RVP. I assume that the note about the jumper deals with this issue...

    The new Dometic digital system will ONLY work with the Dometic thermostat- it is a single comm wire setup, truly digital, not just a digital display on an analog setup, like all of the standard Hunter, et.al.
  • Chris Bryant wrote:
    If you want to use the thermostat you have, you cannot change the board in the air conditioner, only change it if you want to use the Dometic thermostat.
    The Atwood should work with what you have.


    Then how does he wire it.........furnace is only thing working?
  • If you want to use the thermostat you have, you cannot change the board in the air conditioner, only change it if you want to use the Dometic thermostat.
    The Atwood should work with what you have.
  • The Duo Therm T-stat #3107612.008 is obsolete.
    NEW Duo-Therm Dometic Thermostat Part #3106995.032 Must Use With #3107541.009 Relay Kit.

    And that analog t-stat was discontinued.
    Dometic 3313189 Digital Replacement Kit for Dometic 3106995.032 Analog Thermostat

    So you may need the different relay board to use a digital t-stat
  • Old-Biscuit wrote:
    I'm not positive but thought that the control board for that old analog t-stat had to be replaced with one compatible with digital


    According to the instruction sheet it should be able to directly replace an analog thermostat.

  • I'm not positive but thought that the control board for that old analog t-stat had to be replaced with one compatible with digital