BFL13 wrote:
I am not clear whether you have allowed for the proper method of fusing "branches" and the output of a bus to total the amps of all the branches. I assume there are branch fuses not shown: inverter to bus, MPPTs, RV, Victron positive?
This is very good at explaining it all. Worth a look!
http://www.bcae1.com/fuses.htm
I see two batts "bunched" and three separate. I still think 2 and 3 bunched is better, but no proof to hand.
The 2 batteries are not bunched, the drawing software insists on overlaying the lines, they each have their own run to the bus, but share a lug. I'm not sure I understand why fuses would be needed between each battery and the bus if the bus overall is 'protected' by the fuse between the buses?
Thanks for the link!