BFL13
Nov 28, 2018Explorer II
mrad wrote:enblethen wrote:
1200 watts would be about 100 amps.
You could go to auto parts store and get a #2 battery cable with ring terminals on each end.If you have no plans on more load a #4 battery cable would work.
Hmmm... so if I have two 109 hour at @ 1 amp, deep cycle, how long can hope for it to last before falling to 50% discharge ?
EDIT--how will you know you are down to 50%? It is not so easy to tell.
A 27 will have about 90AH at the "20 hour rate" that rate is the current it takes to go from full to empty in 20 hours. So 90/20 = 4.5 amps. So it takes 10 hours at 4.5 amps to get to 50%.
You have two batteries, so now you can go more than twice that 10 hours at 4.5 amps. (Your 20 hour rate is now 9 amps, and you go longer at lower than that rate --Peukert says so)
I don't know the Peukert factor for those batts but say somewhere like 12 hours or so at 4.5 amps?
BTW I think your problem will be generator time recharging that 180AH pair with your little Vector charger at 12 amps. Say you want to go from 50% back up to 90% and stop the gen.
50-90 is 40% of 180 = 72AH and 72/12 = 6 hours. If the gen is on anyway for some other reason that long, then no problem