msiminoff wrote:
timmac,
The problems I have seen and heard about are typically the result of a poor installation and/or insufficient battery capacity.
Based on your description, the problems you are experiencing are a result of low voltage to the inverter. Either you wiring is too small, too long, your batteries cannot provide sufficient current without sagging (I suspect that it is a combination of all three).
Hoping to operate a ~1500W load (e.g. microwave) from a pair of cheap Group 31 FLA batteries without the inverter shutting down is wishful thinking. If you only have room for two batteries, consider two Group 31 AGM's (e.g. Lifeline or Odyssey). More (or larger) batteries is better.
Cheers,
-MS
That is the 2 batts I put in 31 group AGM Durcell Platinum deep cycle, I now have 200 amp hrs, more amps than I did with the 34 group batts, yes I now know the wire feed needs to be larger but at one time it did run my microwave with the smaller batts but it no longer does, that is also not my only problem now, the inverter even shuts off sometimes for no reason, the book says I can hook to power and the inverter will power down, it no longer does this, it trips off, even sometimes it takes out my GFI, maybe I was not posting correct all my issues, maybe I will try 4/0 wire and see what happens but I also suspect the invertor it self is gone bad.
What all the people posting here don't know when I bought this RV almost 2 years ago this system was already in RV and working fine for almost a year than troubles started, since the batts were small and older I thought new stronger better batts would have fixed my problems but it has not.