edatlanta wrote:Chris Bryant wrote:
I measure voltage drop across terminals and cables under load.
This would only test the capacity of the entire system. The OP is looking for a bad connection or undersized wire based on heat built up.
No, this tests each cable and each connection. Why guess using an IR gun when you can *directly* measure the loss with an accurate meter. That's how I measured and found bad crimps- which were heating up- put a couple hundred amps load, and put a volt meter across every connection- not the entire system.
Bad crimp- got hot:

That was wrapped in elecrical tape.
The OP is not going to find a bad connection on the solar side with a heat gun, but he could with a volt meter.