Forum Discussion
da_bees
May 17, 2013Explorer
Jerry B wrote:
Could I just tap into the RV load center and put another sub panel in the laundry room?
You should use equal or larger wire between load center and sub panel as in shore cord. You never want wire with less capacity than the breaker protecting it. For economy and ease of routing wire,I would locate sub as close to load center as possiable.
From load center to sub is wire same or larger than shore cord. Sub is fused to match dryer and wire from sub to dryer matchs breaker. Some of that is mute if dryer pulls max shore cord is rated for.