Forum Discussion
CA_Traveler
Feb 22, 2019Explorer III
For series you need another number:
Voc = 22.8*3 = 67.14V
You MPPT controller maximum input voltage rating must exceed 67V or it will let the smoke out.
AND the controller rating must exceed 67V FOR any temperature. There are calculators for this where you input the panel and your temperature range. Perhaps 80V+.
Voc = 22.8*3 = 67.14V
You MPPT controller maximum input voltage rating must exceed 67V or it will let the smoke out.
AND the controller rating must exceed 67V FOR any temperature. There are calculators for this where you input the panel and your temperature range. Perhaps 80V+.
About Technical Issues
Having RV issues? Connect with others who have been in your shoes.24,201 PostsLatest Activity: Feb 19, 2025