joebedford's avatar
joebedford
Nomad II
Jun 04, 2015
Wot size wire for buried cable to 50A RV receptacle at home?
I'm planning on putting a sub panel in my shop on the side of the house where my RV is stored during the summer. Not worried about the gauge of wire from the main panel to the sub panel - a problem for another day.
I'd like to bury a power cable and install a 50A receptacle right next to the RV. It's going to be about 60 cable-feet from the subpanel to the receptacle on the post.
My hot tub is 60A and the electrician installed and the inspector approved 6 gauge wire for a similar length run.
Is 8 gauge allowed or should I be burying 6 gauge?
I'm planning on burying it in 1-1/2" PVC.
  • Your hot tub is not as voltage sensitive as your R.V.
    Code violation may be costly. Say you experience a damaging electrical event and your insurance is set to foot the bill. All they need to do is send someone to verify the loss....
    Electrical codes exist for your protection.
  • You will never use anywhere near 50A on each leg. Rarely over 25 per leg unless you run microwave, hair dryer and an electric heater.
    You could use dual 30 breakers and drop the wire size to 8. You could still run both ACs microwave and fridge.
  • #8 is good for maybe 10' max. You need #6.
    May need to oversize the conduit if using a bundled cable.
    Are you running from the hot tub sub-panel? Because it may not have a neutral and you must have all 4 wires.
  • I ran #6 copper through 1-1/2" pvc, 24" deep trench for about 100'. My inspector passed that with flying colors. I ran the wire through each 8' section of pvc and then once all wire was through the pvc, I then glued the pvc ends together one at a time in the trench. Trying to run #6 wire through a already glued pvc would be really, really difficult.
    You had better contact your inspector to make absolutely sure on the #8 wire.
    Ron
Having RV issues? Connect with others who have been in your shoes.24,330 PostsLatest Activity: Oct 30, 2025