bobsbbq wrote:
kaydeejay wrote:
FWIW (and not trying to confuse you) a 50A service is in fact TWO 50A services at 110 volts each. That adapter you need will only draw from one side of that 50A service.
Does this mean you could effectively use a total of 70 Amps? Meaning if you had your 30 Amp service for TT and you had a separate box to distribute the 50 Amp service to say electric heaters. The 50 amp circuit would be separate from the 30 Amp.
I thought the service on the pedestal was 50 Amp maximum.
The 50A service at the pedestal is TWO separate 50A services at 110 volts, or a single 50A service at 220volts.
You can slice and dice them any way you want with appropriate adapters and connections.
IOW if you want to break out half that circuit to a separate feed into you unit powering electric heaters, you are perfectly at liberty to do so.
Just watch for current draw in cables that are not rated high enough for the combined current you could draw with multiple heaters. It is theoretically possible to draw 6000 watts from EACH half of a 50A service.