thegabrielles wrote:
Snip...
The RV came prewired for 50Amp so adding a second AC shouldn't be too complicated... except finding one. The specs on the ceiling where the wiring is state: 110-125Volt, 60Hz, and here is my problem 16Amps Maximum. I am struggling to find an AC that will meet the 16Amp minimum (especially on start-up).
I am looking to add heat to that AC as well. I would appreciate any advice or point me in the right direction.
2022 F150 Powerboost Platinum (purchased Nov 2022, ordered May 2022)
2022 Cruiser Aire 28RKS Purchased Aug 2022
Hi,
I would say you may have miss read/understood the max amperage sticker. The sticker is normally talking about the max constant draw. And are you sure it does not state 15 amp? 16 amp seems odd for wiring size.
I have found "most" RV air conditioners will peak over their normal operating max current upon startup. The inrush current on the compressor will go over for a fraction of a second. The AC units have a hard start or other internal capacitors to help deal with this starting spike. And even then, the startup inrush current will still peg almost double or more over the nameplate max operating current of the AC for a fraction of a second.
For example, many campers, even on a 30 amp camper, come with a 20 amp breaker for the AC unit. I can tell you the AC unit will not pull all 20 amps constantly, but the inrush on a 13,5000 BTU RV AC (older Dometic Brisk Air) can be in the 37 amps range. Yet, the measured normal operating amps are 11.5 amps. If you want to see an amp probe measuring what I am talking about, see my post here on the Sunline forum where I cleaned the AC coils.
https://www.sunlineclub.com/forums/f71/cleaning-the-ac-coils-lots-of-pics-10405.htmlHere is something you can also do. With the power off, measure the wire gauge in the ceiling for the 2nd AC hookup. It may be 14 AWG which is standard for a 15-amp circuit. If it is 12 AWG, it would be for a 20 amp circuit.
The circuit breaker has a slight time delay in it that helps cover quick large inrush currents. This is why the 37 amp inrush of a 13,500 BTU AC unit that only runs on 11.5 amps normally starts up just fine, that and the addition of hard start capacitors on the compressor. Slow blow fuses (the old screw-in type) can have longer time delays than circuit breakers. This can be why they picked a 20 amp breaker to power an 11.5 amp constant draw AC unit. The wire in the camper had to be 12 AWG, but the normal current was only 11.5, yet the inrush was 37 amps but was fast enough not to trip a 20 amp breaker. In this case, a 15 amp breaker may have tripped as the inrush is too high for the time delay. They breakers are rated at X times higher than the stated constant current.
Hope this helps
John