pianotuna wrote:
Hi,........
24 amps continuous is what a 30 amp service can handle.
........
If you check manufacturer circuit breaker trip curves, you will see that circuit breakers are rated to run at full rated load indefinitely. Only after they exceed that current rating do they begin to trip. Slightly exceeding the printed rating they will trip after a few seconds or a few minutes. The more the printed current rating is exceeded, the faster they trip.
It is recommended that the expected design load on a circuit breaker to be less than the max rating. But that does not mean it will trip at less than the max rating.
breaker trip curves