joerg68 wrote:
the air moving across the heater transfer system keeps the temp of the burner from not getting far more dangerous for fire potential
I would like to strongly emphasize that. The burner is designed to deliver a certain amount of heat that has to go somewhere. If the blower doesn't transport it away, it will stay there and heat up the furnace. I would not want to find out at what point it ignites the particle board wall of the neighboring cabinet.
But even if that was not the case... A slower fan will take longer to distribute the same amount of heat inside the camper. It might consume less amps when running, but it will run for a longer time. I would assume the fan is already designed by the manufacturer's engineers to work pretty well, so any gain would probably be small.
Two safety features designed into furnace
Sail switch-------closes when adequate air flow for combustion and heat dissipation is achieved
Limit switch------opens on high temp is sensed (typically 180*/190*F)
Low air flow..sail switch opens
High temp in heat exchanger...limit switch opens
Either one causes DC power to be interrupted to circuit board shutting down main flame/ignition