ScottG wrote:
Once a TPO spews hot water because of being over temp, it's shot because there's wax in it that melts. You have to replace it after fixing the root problem.
Where do you get this idea of 'wax' melting? It's not a fire sprinkler.
A T&P valve operates on 2 principles
1) High pressure (150#) overcomes spring pressure opening valve disc off seat and discharges water until pressure drops (125#). Drop in pressure is due to pressure being relieved thru T&P and the influx of cold water
2) High temperature (210*F). The probe is a thermostatic element that expands and lifts the valve disc off the seat relieving the overheated water which allows the influx of cold water. When the temperature cools below 210*F the thermostatic element will contract allowing the spring to close the valve disc against the seat.
And the T&P is ready to function again and again and again on high temp/high pressure situations.
You can (and should yearly) test the valve function by manually opening valve via lever and allow it to snap shut.
There is no wax that melts.