At that distance, if you are really drawing 50 amps then #4 copper is the minimum to have your voltage drop below 3%. If you want to save some money you could run #2 aluminum. However, with just one 30 amp trailer initially the situation isn't as good. Pulling 30 amps at 120v means you would need #3 copper or #1 Aluminum as a minimum to be under 3% voltage drop.
Personally, I would run aluminum to save some money. Also, I put everything underground in conduit. Conduit is cheap versus getting the cable damaged, finding the damage, digging it back, up, etc.
Don't try to pull a multiwire cable thur conduit. That is extremely difficult. You would pull individual wires thru the conduit. Alumiium wiring will be type XHHW, copper will be type THHN.
Individual conductors in conduit are usually less expensive than UF cable and much easier to work with.
Personally, I would run aluminum to save some money. Also, I put everything underground in conduit. Conduit is cheap versus getting the cable damaged, finding the damage, digging it back, up, etc.
Don't try to pull a multiwire cable thur conduit. That is extremely difficult. You would pull individual wires thru the conduit. Alumiium wiring will be type XHHW, copper will be type THHN.
Individual conductors in conduit are usually less expensive than UF cable and much easier to work with.