Feb 06, 2018Explorer III
otrfun wrote:ktmrfs wrote:We had a situation where we had to run 35 ft. of 2/0 cable from a 1000 PSW watt inverter to two GC2 batteries. On a number of occasions we placed a 65 amp load on the batteries with the inverter (~700 watt a/c load) and regularly ran the two GC2 batteries down to 50% SOC with no inverter alarms or shutdowns. Output from the inverter was always stable at 117 vac. DC voltage drop (due to 35 ft. 2/0 cable) with the 65 amp load was approx. .35v (3%). This particular inverter was supposed to alarm at approx. 10.6v and shutdown at approx. 10.0v. It never alarmed or shutdown.
. . . if the pair of GC drops below about 75-80% SOC, you can hit the inverter shutoff limit pretty easy with loads of 800-1000 W. Some may depend on the specific inverter and what it's lower limit is.
Now if the batteriesa are above 80% or so, you in good shape. but that means keeping them near full charge when you want the inverter. So.... run the furnace at night then get up and turn on the toaster.... likely be a nope! low temps= higher internal resistance, lower capacity, coupled with partial discharge.
IMHO if your happy with your current 12V setup, don't mess with it. Or, get GC for most of the stuff and run the inverter off 1 or 2 12V AGM's or similar.
your inverter has a much lower threshold than mine does. mine alarms at 11.5V ad shuts down not much below that. From what BFL experienced I suspect his was similar to mine. You've got about another 1V margin, which would make a big difference. So, the GC work well with your combo. Another story with mine. So, yes sucess (or failure) is highly dependent on both the batteries and inverter.
About Travel Trailer Group
44,060 PostsLatest Activity: Jul 17, 2025