Important thing is to adequately power any sensitive, power hungry devices (Air conditioners, other large draw motors, 12V converter) and be able to maybe power them together. AWG #10 meets the ampacity of 30 amps of current requirement. If having a run of wire close to 100', AWG #8 would be a much better choice.
Rationale for installing a 50 amp pedestal has a lot of merit but costs often overrule best possible solutions. With 50 amp service and the larger wire (also multiple outlets), you would never suffer a loss of power.
Here's a tip for those wanting larger wire: shop a local electrical surplus reseller. Large metro areas typically have at least one reseller in the area. I bought single conductor AWG 6 with a very good jacket for $.50/ft, recently.
FWIW, I used two lengths of this to power a 50 amp subpanel, the ground terminated at the subpanel location. The subpanel powers a welder receptacle, my 50 amp RV receptacle, and 4 x 15 amp 120V receptacles. Yes, I'm kind of cheating on the total ampacity, but none are all used at the same time and I'm using a larger load center box.
Rationale for installing a 50 amp pedestal has a lot of merit but costs often overrule best possible solutions. With 50 amp service and the larger wire (also multiple outlets), you would never suffer a loss of power.
Here's a tip for those wanting larger wire: shop a local electrical surplus reseller. Large metro areas typically have at least one reseller in the area. I bought single conductor AWG 6 with a very good jacket for $.50/ft, recently.
FWIW, I used two lengths of this to power a 50 amp subpanel, the ground terminated at the subpanel location. The subpanel powers a welder receptacle, my 50 amp RV receptacle, and 4 x 15 amp 120V receptacles. Yes, I'm kind of cheating on the total ampacity, but none are all used at the same time and I'm using a larger load center box.