Coach-man wrote:
Well which is it? Are they the same or differant? I double checked my calculations online with NEC, and stand by their minimum requirements, none the less you have already contradicted yourself, the lack of knowledge about how electricity works makes you wonder!
โMay-23-2015 07:16 AM
klassic wrote:Me Again wrote:
The way a four wire 240V circuit works you have a ground, neutral, and two 120 hot phases. 240V appliances just use the two hots and ground. A 120V appliance uses one or the other hot and neutral. If neutrals path to the reference source is broken, then a 120V finds the path to the other 120V phase and you have 240 across the appliances, smoke and smell.
Ecample.
Refer on phase one and neutral =120V
Microwave on phase two and same neutral = 120V
Neutral burns up in at power pole(common occurrence). Phase one comes in on hot lead to refer and goes out neutral, then finds no route to source. It does however find a route via the microwave's neutral and on out to the other phase 120V. 120+120=240 volts across the two devices. Repeats across other devices on the two source phases. Low resistance devices burn up one after another working towards higher resistant devices.
Chris
Sorry about the hijack
I understand your example.... But wouldn't the main ground wire have to burn up too for this to happen?
If I yank the neutral wire out of my home's service panel... All the circuit's neutrals still tie into ground.
Or are RV panels wired differently?
โMay-23-2015 07:06 AM
Coach-man wrote:
The original question was can I plug a 30 amp RV into a 50 amp outlet, the answer was yes with an adaptor! Someone, mentioned that, that was dangerous, it is not, in fact several posts indicated that is was less likely to have a problem, brownouts, triped circuit breakers, etc by plugging into the 50 amp outlet, too which I agreed. At least one person disagreed and went into an esoteric discussion on wiring, and that it was the same regardless of which plug was used. I disagreed and continue to disagree! A "50 amp" plug is actually 100 amps total, that is two 120 volt 50 amp feeds with a common neutral. You can get real close to overloading a 30 amp circuit, but you have more cushion, with a 50 in a rig designed for 30 amp service. If there is a problem, your main circuit breaker in the rig would blow long before your pedistal breaker would go, and no you can not draw more than the maximum of 30 amps, and in a 30 amp rig with adaptor there is no way of seeing 240 volts in your rig! Even in a 50 amp rig, 240 volts to your equipment would be unlikely due to the fourth lead, ie ground!
โMay-23-2015 07:05 AM
Me Again wrote:
The way a four wire 240V circuit works you have a ground, neutral, and two 120 hot phases. 240V appliances just use the two hots and ground. A 120V appliance uses one or the other hot and neutral. If neutrals path to the reference source is broken, then a 120V finds the path to the other 120V phase and you have 240 across the appliances, smoke and smell.
Ecample.
Refer on phase one and neutral =120V
Microwave on phase two and same neutral = 120V
Neutral burns up in at power pole(common occurrence). Phase one comes in on hot lead to refer and goes out neutral, then finds no route to source. It does however find a route via the microwave's neutral and on out to the other phase 120V. 120+120=240 volts across the two devices. Repeats across other devices on the two source phases. Low resistance devices burn up one after another working towards higher resistant devices.
Chris
โMay-23-2015 06:33 AM
โMay-22-2015 10:13 PM
โMay-22-2015 10:31 AM
Me Again wrote:
...
The worst condition people face is those with full 50 service. If the neutral lead goes bad, then 240V is placed across everything in the trailer or coach, and you burn up TVs, micro waves, converters, inverters, stereos, and sat equipment. Friend had that happen this winter in California. His bill to date is 7K and they are not done replacing things.
If you have full 50 service, have a good isolation device that will protect you from this happening.
"The lack of knowledge about how electricity works makes you wonder???"
Chris
โMay-21-2015 06:15 PM
โMay-21-2015 05:57 PM
Coach-man wrote:
30 amp and 50 amp uses the same wiring? 30 amp uses 12 gauge wire, 50 amp uses 10 gauge wire! They better not be using the same wires! I guess some parks will try and get by using the same wires, but that is so wrong! It is far more common to have a 30 amp overheat than a 50 amp. Now, if you are using a full 50 amps, and there is a brownout, you may be in trouble, and you should be using some sort of protection to avoid burning out AC compressors and or expensive electronics! But a 30 amp RV plugged into a 50 amp circuit, would have more of a cushion than a 50 amp, not to say an isolation transformer or some other protection should be avoided.
โMay-21-2015 05:52 PM
Old-Biscuit wrote:Me Again wrote:
Just remember that you will have a 50 breaker feeding #10 30amp rated cable, so if you have a problem ahead of the trailers 30 main breaker, you could have an electrical fire risk. Chris
But you can only draw 30A regardless of 50A service.....cause over 30A trailer main 30A breaker will trip and no more amp draw
Course what if.....50a receptacle shorted, or plug broke off or tree falls on power pedestal or squirrel chews on cord
โMay-21-2015 05:50 PM
โMay-21-2015 05:26 PM
Me Again wrote:Coach-man wrote:
The 50 amp service is over what you need for your 30 amp rig, one it should be more stable, two at 50 amps even if it is overloaded from too many other 50 amp rigs in the park you should have no problems with using 30 amps! The adaptor is less than $20, well worth the price! No worries you can not use more than the 30 amps that your rig is rated for! If there should be a fault your 30 amp circuit breaker will kick in and handle the emergency, and that would be a problem un related to your using the 50 amp plug!! The lack of knowledge about how electricity works makes you wonder???
The 50 amp outlets are power by the same conductors that the 30 outlets are powered from. If the park is having brownout conditions(which is low voltage because of load, and more amps are trying to flow to make up for it) on one or both of the power legs of a 50 outlet, that same condition will be occurring on the single leg of a 30 amp outlet if brownout is on both legs or on the single leg if 30 amp outlet and you are on the same brownout leg. The 30amp outlets if wired correctly should be alternating site to site
between the two legs of the parks power distribution.
The worst condition people face is those with full 50 service. If the neutral lead goes bad, then 240V is placed across everything in the trailer or coach, and you burn up TVs, micro waves, converters, inverters, stereos, and sat equipment. Friend had that happen this winter in California. His bill to date is 7K and they are not done replacing things.
If you have full 50 service, have a good isolation device that will protect you from this happening.
"The lack of knowledge about how electricity works makes you wonder???"
Chris
โMay-21-2015 11:39 AM
โMay-21-2015 08:56 AM
Me Again wrote:Coach-man wrote:
The 50 amp service is over what you need for
The 50 amp outlets are power by the same conductors that the 30 outlets are powered from. If the park is having brownout conditions(which is low voltage because of load, and more amps are trying to flow to make up for it) on one or both of the power legs of a 50 outlet, that same condition will be occurring on the single leg of a 30 amp outlet if brownout is on both legs or on the single leg if 30 amp outlet and you are on the same brownout leg. The 30amp outlets if wired correctly should be alternating site to site between the two legs of the parks power distribution.
"The lack of knowledge about how electricity works makes you wonder???"
30 amp and 50 amp uses the same wiring? 30 amp uses 12 gauge wire, 50 amp uses 10 gauge wire! They better not be using the same wires! I guess some parks will try and get by using the same wires, but that is so wrong! It is far more common to have a 30 amp overheat than a 50 amp. Now, if you are using a full 50 amps, and there is a brownout, you may be in trouble, and you should be using some sort of protection to avoid burning out AC compressors and or expensive electronics! But a 30 amp RV plugged into a 50 amp circuit, would have more of a cushion than a 50 amp, not to say an isolation transformer or some other protection should be avoided.
And my quote, about the lack of knowledge was not directed to the OP, it was directed to the person who stated there was imminent danger of plugging a 30 amp rig using an adaptor into a 50 amp plug!
โMay-21-2015 06:43 AM
Coach-man wrote:
The 50 amp service is over what you need for your 30 amp rig, one it should be more stable, two at 50 amps even if it is overloaded from too many other 50 amp rigs in the park you should have no problems with using 30 amps! The adaptor is less than $20, well worth the price! No worries you can not use more than the 30 amps that your rig is rated for! If there should be a fault your 30 amp circuit breaker will kick in and handle the emergency, and that would be a problem un related to your using the 50 amp plug!! The lack of knowledge about how electricity works makes you wonder???