Dometic 5 button thermostat replacing a 4 button

We have a 2000 Dutch star diesel pusher 40 ft. We replaced the thermostat with a newer 5 button model had to replace the circuit boards on the air conditioners as well with googles help we got the air conditioner and heat pump on zone 1 to work but the furnace is not being recognized and I can't change it to zone 2 help
  • You have to set the rear AC control board DIP switch to Zone 2 on the circuit board and the HP DIP to on. The Zone 1 DIP switch for furnace must be set to ON. Then you do a reset for the wall 5 button to see the settings. Doug