down home wrote:50A RV power IS 240/120V. Most RV's don't have 240V appliances.
This is important because you don't want to destroy your mh electric by plugging into a 240 volt pug as quite a few have.
We don't have 50 amp 240 volt service. You have two 50 amp legs and a common ground. 100 amps total but on two legs unless you have a Prevost or other with two fifty amp cables and 100 amp service.
Don't hit your mh with 240 Volts. It might burn up but will msot certainly be expensive if the breakers can't handle it.
โDec-18-2017 12:23 PM
down home wrote:rhagfo wrote:Bill.Satellite wrote:rhagfo wrote:Bill.Satellite wrote:
If they are talking about the Cheap Heat system it IS 5000 watts and requires 50 amp service as it does draw somewhere close to 40 amps. Nothing cheap about that if you have to pay the electric bill.
If you donโt know what you are talking about, you should stay out of the discussion!
#1. It DOESN'T require a 50 amp service to operate, on the 1,800 watt setting it works on a 30 amp service, through a 20 amp breaker.
#2. On the 5,000 watt setting, yes a 50 amp 208 volt service is required, but the system runs on a 30 amp 208 volt breaker.
We have a 32โ 5er the we heated to 70 degrees easily with outside temperatures in the low fortyโs on the 1,800 watt setting on a 30 amp service used other electrical device without issues.
Currently on a 50 amp service, and the 5,000 watt setting and will heat us down in to the teens.
I am seriously considering the new add on box that auto detects the voltage 120/208 and switches to the correct wattage for the service one is connected to. I can manually change over in about 20 minutes, but having it do it automatically would be nice.
It doesnโt make any difference if use cheap heat or electric space heaters, you are still using electricity so the bill will be the same. My furnace doesnโt run continuously cycles just like using gas.
Thanks for the kind thoughts! Also, thanks for confirming that you are going to need 50 amp service if you plan to use the 5000W option. There is NO 208 V service available with 30 amp service. Don't you hate it when that happens!
Yep, sure do!!:S
I looked in to this closely before deciding to install. Several emails to the developer. Once I realized that the package was one set of components, just wired differently, I decided to buy.
As I have stated I have wiring for both 30 amp 120 volt and 50 amp 240 volt installed, and it takes about 20 minutes of work to switch. RV Comfort Systems now offer an auto switch device for $119, which I am seriously thinking of installing to save the time and effort.
I am still impressed with how well it works, I had done the watts to BTU previous to buying, I knew my gas furnace rated at 30,000 BTU INPUT, was only rated at 23,700 BTU OUTPUT. That is still better than the 17,060 BTU on 5,000 watt setting, so far it does the job of keeping us warm.
One of the nicer features is that heat is almost instant, there is no 15 second purge, the element gets power the same time the fan starts, the only cool air you feel is what is in the duct.
My personal reason,for buying was mainly SAFETY, I am the son of a Firefighter, he disliked winter, too many fires caused by space heaters and from time to time death. Secondary to that is my heater doesn't take up any floor or counter space.
This is important because you don't want to destroy your mh electric by plugging into a 240 volt pug as quite a few have.
We don't have 50 amp 240 volt service. You have two 50 amp legs and a common ground. 100 amps total but on two legs unless you have a Prevost or other with two fifty amp cables and 100 amp service.
Don't hit your mh with 240 Volts. It might burn up but will msot certainly be expensive if the breakers can't handle it.
โDec-18-2017 11:52 AM
rhagfo wrote:Bill.Satellite wrote:rhagfo wrote:Bill.Satellite wrote:
If they are talking about the Cheap Heat system it IS 5000 watts and requires 50 amp service as it does draw somewhere close to 40 amps. Nothing cheap about that if you have to pay the electric bill.
If you donโt know what you are talking about, you should stay out of the discussion!
#1. It DOESN'T require a 50 amp service to operate, on the 1,800 watt setting it works on a 30 amp service, through a 20 amp breaker.
#2. On the 5,000 watt setting, yes a 50 amp 208 volt service is required, but the system runs on a 30 amp 208 volt breaker.
We have a 32โ 5er the we heated to 70 degrees easily with outside temperatures in the low fortyโs on the 1,800 watt setting on a 30 amp service used other electrical device without issues.
Currently on a 50 amp service, and the 5,000 watt setting and will heat us down in to the teens.
I am seriously considering the new add on box that auto detects the voltage 120/208 and switches to the correct wattage for the service one is connected to. I can manually change over in about 20 minutes, but having it do it automatically would be nice.
It doesnโt make any difference if use cheap heat or electric space heaters, you are still using electricity so the bill will be the same. My furnace doesnโt run continuously cycles just like using gas.
Thanks for the kind thoughts! Also, thanks for confirming that you are going to need 50 amp service if you plan to use the 5000W option. There is NO 208 V service available with 30 amp service. Don't you hate it when that happens!
Yep, sure do!!:S
I looked in to this closely before deciding to install. Several emails to the developer. Once I realized that the package was one set of components, just wired differently, I decided to buy.
As I have stated I have wiring for both 30 amp 120 volt and 50 amp 240 volt installed, and it takes about 20 minutes of work to switch. RV Comfort Systems now offer an auto switch device for $119, which I am seriously thinking of installing to save the time and effort.
I am still impressed with how well it works, I had done the watts to BTU previous to buying, I knew my gas furnace rated at 30,000 BTU INPUT, was only rated at 23,700 BTU OUTPUT. That is still better than the 17,060 BTU on 5,000 watt setting, so far it does the job of keeping us warm.
One of the nicer features is that heat is almost instant, there is no 15 second purge, the element gets power the same time the fan starts, the only cool air you feel is what is in the duct.
My personal reason,for buying was mainly SAFETY, I am the son of a Firefighter, he disliked winter, too many fires caused by space heaters and from time to time death. Secondary to that is my heater doesn't take up any floor or counter space.
โDec-17-2017 03:21 PM
โDec-17-2017 02:36 PM
โDec-17-2017 01:56 PM
โDec-17-2017 05:50 AM
โDec-17-2017 05:41 AM
Bill.Satellite wrote:rhagfo wrote:Bill.Satellite wrote:
If they are talking about the Cheap Heat system it IS 5000 watts and requires 50 amp service as it does draw somewhere close to 40 amps. Nothing cheap about that if you have to pay the electric bill.
If you donโt know what you are talking about, you should stay out of the discussion!
#1. It DOESN'T require a 50 amp service to operate, on the 1,800 watt setting it works on a 30 amp service, through a 20 amp breaker.
#2. On the 5,000 watt setting, yes a 50 amp 208 volt service is required, but the system runs on a 30 amp 208 volt breaker.
We have a 32โ 5er the we heated to 70 degrees easily with outside temperatures in the low fortyโs on the 1,800 watt setting on a 30 amp service used other electrical device without issues.
Currently on a 50 amp service, and the 5,000 watt setting and will heat us down in to the teens.
I am seriously considering the new add on box that auto detects the voltage 120/208 and switches to the correct wattage for the service one is connected to. I can manually change over in about 20 minutes, but having it do it automatically would be nice.
It doesnโt make any difference if use cheap heat or electric space heaters, you are still using electricity so the bill will be the same. My furnace doesnโt run continuously cycles just like using gas.
Thanks for the kind thoughts! Also, thanks for confirming that you are going to need 50 amp service if you plan to use the 5000W option. There is NO 208 V service available with 30 amp service. Don't you hate it when that happens!
โDec-17-2017 03:17 AM
rhagfo wrote:Bill.Satellite wrote:
If they are talking about the Cheap Heat system it IS 5000 watts and requires 50 amp service as it does draw somewhere close to 40 amps. Nothing cheap about that if you have to pay the electric bill.
If you donโt know what you are talking about, you should stay out of the discussion!
#1. It DOESN'T require a 50 amp service to operate, on the 1,800 watt setting it works on a 30 amp service, through a 20 amp breaker.
#2. On the 5,000 watt setting, yes a 50 amp 208 volt service is required, but the system runs on a 30 amp 208 volt breaker.
We have a 32โ 5er the we heated to 70 degrees easly with outside temperatures in the low fortyโs on the 1,800 watt setting on a 30 amp service used other electrical device without issues.
Currently on a 50 amp service, and the 5,000 watt setting and will heat us down in to the teens.
I am seriously considering the new add on box that auto detects the voltage 120/208 and switches to the correct wattage for the service one is connected to. I can manually change over in about 20 minutes, but having it do it automatically would be nice.
It doesnโt make any difference if use cheap heat or electric space heaters, you are still using electricity so the bill will be the same. My furnace doesnโt run continuously cycles just like using gas.
โDec-16-2017 09:51 PM
pianotuna wrote:
First, try not to be rude.
2nd 1800 watts only yields about 6141 btu's. Not nearly enough to keep warm in serious cold. It is only 1023 btu's better than a 1500 watt heater from Walmart which costs $9.99. Or you could use one 1500 watt and add a 1000 watt heater. That yields 8530 btu's, and leaves enough head room to run the fridge on the electric setting.
3rd the 3750 watt only does 12795 btu's. That's a little better but still not what I'd call wonderful.
4th the 5000 watt only does 17060 btu's. It is unclear to me whether they wire this as a balanced load. Perhaps you could enlighten us?
5th if the voltage sags (and it will), you won't get nearly the same amount of heat.
6th, in order to successfully heat my RV at -27 c (-16.6 f) I require up to 7000 watts of electricity (peak load 23884 btu's). I do use a sola basic autoformer to keep the voltage up on the OEM 30 amp service, and have added 20 amp and 15 amp auxiliary shore power cords which I run from a 50 amp "break out box".
So the Cheap Heat is not terrible useful to anyone who lives where there is serious cold, partly because it may not be run in parallel with the propane furnace. Nor does it fail over to propane heating if the power goes off.
BTW where I live it gets to -40. That means I've added extra insulation, Insulbright covers for all windows, vents, skylights and doors. Other cold weather modifications include adding insulated pillows for vents and skylights. I've also added an Insulbright divider to eliminate heating the cab on my class C.rhagfo wrote:
If you donโt know what you are talking about, you should stay out of the discussion!
#1. It DOESN'T require a 50 amp service to operate, on the 1,800 watt setting it works on a 30 amp service, through a 20 amp breaker.
#2. On the 5,000 watt setting, yes a 50 amp 208 volt service is required, but the system runs on a 30 amp 208 volt breaker.
We have a 32โ 5er the we heated to 70 degrees easly with outside temperatures in the low fortyโs on the 1,800 watt setting on a 30 amp service used other electrical device without issues.
Currently on a 50 amp service, and the 5,000 watt setting and will heat us down in to the teens.
โDec-16-2017 06:48 PM
AllegroD wrote:
Lot of good ideas here but do not forget that your wet bay is likely NOT going to receive enough heat to keep from freezing your fresh water tank and lines. Your gas furnace does that.
โDec-16-2017 06:43 PM
rhagfo wrote:
If you donโt know what you are talking about, you should stay out of the discussion!
#1. It DOESN'T require a 50 amp service to operate, on the 1,800 watt setting it works on a 30 amp service, through a 20 amp breaker.
#2. On the 5,000 watt setting, yes a 50 amp 208 volt service is required, but the system runs on a 30 amp 208 volt breaker.
We have a 32โ 5er the we heated to 70 degrees easly with outside temperatures in the low fortyโs on the 1,800 watt setting on a 30 amp service used other electrical device without issues.
Currently on a 50 amp service, and the 5,000 watt setting and will heat us down in to the teens.
โDec-16-2017 05:16 PM
โDec-16-2017 04:47 PM
Bill.Satellite wrote:
If they are talking about the Cheap Heat system it IS 5000 watts and requires 50 amp service as it does draw somewhere close to 40 amps. Nothing cheap about that if you have to pay the electric bill.
โDec-16-2017 02:23 PM
AllegroD wrote:I use small 100watt heaters plugged into thermo cubes to keep the wet bays from freezing.
Lot of good ideas here but do not forget that your wet bay is likely NOT going to receive enough heat to keep from freezing your fresh water tank and lines. Your gas furnace does that.