ScottG wrote:dougrainer wrote:RCMAN46 wrote:
The 50 amp 220 volt is the same as the 30 amp 220 volts at your home.
Most RV's loads are 110 volts thus only use one side of the 220 volts as do most of the loads at your home. Most homes only the water heater, electric range and electric furnace use 220 volts and most are 30 amps or less with the exception of some heat pumps. A heat pump in a RV may be wired for 220 volts.
NO HP in a RV is wired for 220 volts. No such HP for an RV has 220 volts. ALL are 110 volts.
220/240 volts in an RV is supplied by 2 separate 120 wires OUT OF PHASE. EACH side is on a 50 amp breaker for 100 amps total supply. The RV does NOT separate the supply. The supply is already separated at the POLE. If the Supply is in phase, the RV will not function correctly all the time. For instance, you have a built in EMS (energy management system) . IT sees if the supply is out of phase. IF IT IS, then you have full 100 amp capacity. IF same phase at supply the EMS will only allow 30 amps total operation. It assumes you have connected a 50 to 30 amp reducer dogbone. IF you think you are connected to a 50 amp service and your EMS shows 30 amp, you have what I call CHEATED 50 amp service. The RV park did not upgrade their supply and wiring for true 50 amp total 100 amp service. This is theft by the RV park. You are paying for 50 amp service and they are NOT giving you what you pay for. The simple test ALL RV'ers need to do is have a multitester and at the Park Pole test the voltage between the 3 and 9 o clock spade slots. 50 amp will show 240. ANY OTHER reading, the pole is NOT 50 amp. Doug
A good explanation. Only thing wrong with it is that the "out of phase" part - a common misconception.
They (the two legs) are in-phase with each other and maybe easier to understand as two halves of the same phase. On an oscilloscope the signal would look like one complete sine wave. That phase is then split into the two, 120VAC legs.
So your 240VAC service is referred to as Split-Phase.
โJan-02-2023 05:25 AM
โJan-02-2023 02:36 AM
โJan-01-2023 06:16 PM
valhalla360 wrote:Yes the 12,000 watts would have to be split perfectly half to each side. Still available and would be eight 1500w space heaters if all are on separate branch circuits and four on each side.time2roll wrote:
12,000 watts of electric power available.
Minor nitpick.
You have 2legs @ 6000w.
If you try to pull 8000w on leg 1 and 4000w on leg 2, expect it to pop the breaker.
Of course, that's a lot of power, so unless you are running several space heaters, it's not likely to happen.
โJan-01-2023 06:09 PM
dougrainer wrote:RCMAN46 wrote:
The 50 amp 220 volt is the same as the 30 amp 220 volts at your home.
Most RV's loads are 110 volts thus only use one side of the 220 volts as do most of the loads at your home. Most homes only the water heater, electric range and electric furnace use 220 volts and most are 30 amps or less with the exception of some heat pumps. A heat pump in a RV may be wired for 220 volts.
NO HP in a RV is wired for 220 volts. No such HP for an RV has 220 volts. ALL are 110 volts.
220/240 volts in an RV is supplied by 2 separate 120 wires OUT OF PHASE. EACH side is on a 50 amp breaker for 100 amps total supply. The RV does NOT separate the supply. The supply is already separated at the POLE. If the Supply is in phase, the RV will not function correctly all the time. For instance, you have a built in EMS (energy management system) . IT sees if the supply is out of phase. IF IT IS, then you have full 100 amp capacity. IF same phase at supply the EMS will only allow 30 amps total operation. It assumes you have connected a 50 to 30 amp reducer dogbone. IF you think you are connected to a 50 amp service and your EMS shows 30 amp, you have what I call CHEATED 50 amp service. The RV park did not upgrade their supply and wiring for true 50 amp total 100 amp service. This is theft by the RV park. You are paying for 50 amp service and they are NOT giving you what you pay for. The simple test ALL RV'ers need to do is have a multitester and at the Park Pole test the voltage between the 3 and 9 o clock spade slots. 50 amp will show 240. ANY OTHER reading, the pole is NOT 50 amp. Doug
โJan-01-2023 04:31 PM
time2roll wrote:
12,000 watts of electric power available.
โJan-01-2023 12:14 PM
David0725 wrote:
Can someone explain how the 50 approach system works? Normally 50 amp is 220 but the rv is not 220 its 110 riright? So how does this work?
โJan-01-2023 11:03 AM