My Onan 7000 generator will start and run for about 4 minutes and then cut off. Check the Oil and it is full and the oil switch was disconnected to check if the oil switch was bad, however it is ok. After it cut off it blinks 3 times. Any info is appreciated.
5 REPLIES 5

crasster
Explorer II
Explorer II
It's seriously making me wonder if generators were better when they were not so computerized.

I'm curious if it is an exact 4 minutes, or "4 minutes" for the carb bowl to empty
4 whopping cylinders on Toyota RV's. Talk about great getting good MPG. Also I have a very light foot on the pedal. I followed some MPG advice on Livingpress.com and I now get 22 MPG! Not bad for a home on wheels.

mikestock
Explorer
Explorer
You have not stated if your's is a diesel or gasoline model. Also, who is the rv manufacturer?

The reason I bring this up is that mine did this. I don't recall the second digit of the code but it ended up being a clogged fuel filter. Seems that Tiffin saw fit to install a small inline filter ahead of the Onan, built-in, fuel filter. The Cumins/Onan shop said to always take this little filter out and actually gave me an insert line to replace it. They seem perplexed as to why Tiffin does this and say they do nothing but cause unnecessary problems.

bluwtr49
Explorer II
Explorer II
When mine did that I found it was a loose fan belt and it was shutting down on overheat. The high temp sensor also has a history of failure and will cause the same shutdown.

Easy fix if you don't have to pull the gen set for access like I did.
Dick

2002 43' DP Beaver Marquis Emerald Cat C-12 505 HP, 1600 Tq
2003 Jeep Grand Cherokee Overland ---toad

lc0338
Explorer
Explorer
The Start / Stop / Prime Button will Blink out a Fault Code if the Generator quits running or won't start for whatever reason. The Fault Codes and what they mean are Listed in the Owners Manual.

This is how you read a Fault Code.

1. If you'll look at the Start/Stop Button when the Generator stops running, it will be blinking, there will be a pause and then it will blink the same number of blinks again. Count the Blinks. 3 Blinks indicates a Service Fault. Press Stop and it will start blinking again. What you're looking for is a two digit code. 3 Blinks was the 1st Level of the code, pressing Stop will give you the full code. Example, when you press stop, you'll see, blink, blink, blink - pause - blink, blink, blink, blink, blink, blink - pause, and the blinking repeats it's self. So what code did it blink out? Right 36.

The first set of Blinks that you see when the Generator stops "is" the first Level of the Code, or in the upper example 3. Don't misread the first level blinking as being a 33 or 44. For this reason there is not a Fault Code 33 or 44.

First Level Fault Codes are 3 and 4.
Fault Code 3 is a Service fault. From here you'll look for the second digit code.
Fault Code 4, is caused by Over-cranking.

Now, if you've been gone and when you get back and the generator has stopped running, the Start/Stop Button will not be blinking. It quits blinking after 5 min. To get the Fault Code, Press Stop 3 times within 5 seconds and the blinking will start. You just need to count the First and Second Level Blinks. Example, blink, blink, blink - pause - blink, blink, blink, blink, blink, blink - pause - and it repeats. If you hit stop again, the blinking will Stop.

Onan Fault Codes