BFL13 wrote:
Is the shunt not for a Trimetric monitor? Read the installation manual--it is quite clear on what goes where. Shunts go on the neg side. BTW you want the 500a shunt for the higher amps the inverter will draw, not the 100a.
The inverter wiring is for the amps you will see. The surge rating is for a very short moment that might happen. The fuse on the pos is supposed to protect the wires in that case, like an ANL fuse will not blow right off, but gives a moment for the surge to go away before it blows but then it will if it stays on.
Others might correct me on that but they would have to explain it, which is ok if they do.
โJun-06-2017 05:46 PM
โJun-06-2017 05:41 PM
โJun-06-2017 05:38 PM
BFL13 wrote:
That neg from battery to frame needs to be changed to go to the outer end of the shunt along with all the other negs. Only thing from battery neg is one fat (or double thinner) wire(s) to the inner end of the shunt.
The shunt outer end can't hold all those negs, so you need a neg buss bar to hold a bunch of negs, then a fat wire from the neg buss to the outer end of the shunt.
Double #2 short wire is huge. Can't see any point in going fatter single. Just have to reduce the ends anyway to fit the inverter and converter terminals. Vector 2000w (4000w surge) inverter specifies a wiring kit of twin #4 three feet long. Twin #2 is way more than that. Holy cow. The inverter is 1800, less than 2000.
Of course if you have a run of much more than 3 feet distance, say over 6 ft (one way) you would have to go fatter wire.
โJun-06-2017 05:32 PM
2oldman wrote:
For a 1200w appliance, this is what the approximate amperages to the inverter look like in your setup:
Before we get too involved in this, please share with us what will be the largest loads on your inverter.
โJun-06-2017 05:19 PM
โJun-06-2017 05:14 PM
โJun-06-2017 05:11 PM
2oldman wrote:
Sure about what.. the ampacity? I just looked it up. I thought that was why you were doubling up on them. Did I read that right?
โJun-06-2017 04:57 PM
โJun-06-2017 04:55 PM
2oldman wrote:DiskDoctr wrote:I thought your plan of 2-2awg would be fine. 4/0 is real bear to work with, and is only needed for big draw stuff like extended MW use and maybe coffee makers - which 4 batteries can only handle comfortably for relatively short periods.
So it looks like I need to jump to 4/0 wires?
The ampacity of 2 2awgs is almost the same as 4/0..assuming they work in parallel as you're hoping they will.
โJun-06-2017 04:39 PM
DiskDoctr wrote:I thought your plan of 2-2awg would be fine. 4/0 is real bear to work with, and is only needed for big draw stuff like extended MW use and maybe coffee makers - which 4 batteries can only handle comfortably for relatively short periods.
So it looks like I need to jump to 4/0 wires?
โJun-06-2017 04:22 PM
โJun-06-2017 04:16 PM
time2roll wrote:
IIRC Xantrex recommends 4/0 minimum wire.