JBarca wrote:Cptnvideo wrote:
JBarca, are you saying there are 2 A/C breakers (both turned on) but only one A/C unit?
Sounds like someone could get electrocuted.
I also think you meant a 30 to 50 amp adapter. Putting a jumper between to 2 hots on a 50 to 30 amp adapter would create a major issue.
There may be a play on words, yes, there is only one AC unit on the camper. Yes, there are 2 circuit breakers for 2 AC units as shown on the power panel tags, and yes both are flipped on.
And while they may have run the wire through the camper for a second AC to later add a 2nd AC, that does not mean the wire is connected to the breaker. Keystone made the camper, why they did not label the 20 amp breakers as living area AC, and the other, a future Bedroom AC , I have no idea.
To the 30 to 50 amp adapter, I was referring to a 30 amp male plug on one end and a 50 amp receptacle on the other end, which has the jumper between the 2 hot wires on the 50 amp receptacle end to the one 30 amp hot wire.
This is what Camco calls the 30amp to 50 amp, it is just they do list it as 30M to 50F with the male and female called out. https://www.camco.net/adapters-dogbones/power-grip-18-30am-50af-dogbone-adapter-125v-3750w-cetl-5518...
Re-reading what I posted, while I did call out that the 50 amp end receptacle has the jumper, I may have mixed up the 50 to 30 generic wording. Thanks for pointing that out. I will correct the post to make it more clear. Not sure how you assumed the other way around, but I can see it now being miss read that way. I'll fix it. Thanks
โJun-06-2023 06:12 AM
Terry 25 wrote:
Bobbo: Is your answer still "Yes"? Thanks again to all who replied.
โJun-05-2023 08:14 PM
โJun-05-2023 06:55 PM
Terry 25 wrote:I thought 50a twist lock on an RV had three blades and the ground as a side contact.
OP here. Power cord is 50mp at the pedestal end and a 3 prong twist lock at the trailer end. Main breaker in camper is 30 amp. Since the trailer is on a permanent site I'll just continue to use the 50/30 adapter.
The question remains, hypothetically speaking, if I was on the road could I plug into the 50 amp receptacle on the pedestal without damaging my trailer
โJun-05-2023 06:33 PM
Terry 25 wrote:
The question remains, hypothetically speaking, if I was on the road could I plug into the 50 amp receptacle on the pedestal without damaging my trailer
โJun-05-2023 05:48 PM
โMay-17-2023 12:53 PM
Cptnvideo wrote:
JBarca, are you saying there are 2 A/C breakers (both turned on) but only one A/C unit?
Sounds like someone could get electrocuted.
I also think you meant a 30 to 50 amp adapter. Putting a jumper between to 2 hots on a 50 to 30 amp adapter would create a major issue.
โMay-17-2023 11:00 AM
โMay-17-2023 10:55 AM
Terry 25 wrote:
Just bought a Puma 25BHFQ. One A/C and a 30 amp camper in every way but the plug and cord are 50 amp. Must I always use an adapter or can I plug into 50 amp if available? Thanks. The camper is on a permanent site with a 30 amp plug. I'd like to eliminate the adapter by installing a 50 amp plug.
โMay-17-2023 09:20 AM
Terry 25 wrote:
Just bought a Puma 25BHFQ. One A/C and a 30 amp camper in every way but the plug and cord are 50 amp. Must I always use an adapter or can I plug into 50 amp if available? Thanks. The camper is on a permanent site with a 30 amp plug. I'd like to eliminate the adapter by installing a 50 amp plug.
โMay-17-2023 07:04 AM
Terry 25 wrote:
OP here. Going to camper next week. I'll check camper plug and breaker box and update when I get back. In the meantime, I'll use the adapter. Thanks for the thoughtful replies.
โMay-17-2023 05:41 AM
โMay-17-2023 02:40 AM